Shawn Philip Nelson
Veteran
Has anyone tried striking a 2.5kw Magnetic HMI from the EU3000is Honda genny?
According to the Honda specs that genny can do 25a max or 23a rated, and according to the LTM website (I recently purchased a used LTM 2.5kw Par) the light will draw 26amps at 120v. But this makes no sense! How the heck does 2500w (20.83 amps) draw 26 amps? An old gaff I talked to said he actually runs a 2.5kw off a 20amp industrial socket all the time, says it only draws 26amps at strike and that it's not enough to trip the breaker then you're down around 21-22 amps and fine.
Any experiences here?
According to the Honda specs that genny can do 25a max or 23a rated, and according to the LTM website (I recently purchased a used LTM 2.5kw Par) the light will draw 26amps at 120v. But this makes no sense! How the heck does 2500w (20.83 amps) draw 26 amps? An old gaff I talked to said he actually runs a 2.5kw off a 20amp industrial socket all the time, says it only draws 26amps at strike and that it's not enough to trip the breaker then you're down around 21-22 amps and fine.
Any experiences here?